TME temperature readings?

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • velosprinter
    Junior Member
    • Jul 2008
    • 19

    #1

    TME temperature readings?

    Has anyone here set up a trigger to read temperatures from a Papouch TME Ethernet sensor?

    It has SNMP and I get some results from $snmpwalk -v 1 -c public <IP>

    I also found in a manual:
    MIB Table
    Temperature as number
    Name: int_temperature
    Object ID: 1.3.6.1.4.1.18248.1.1.1
    GET address: 1.3.6.1.4.1.18248.1.1.1.0
    Description: The measured temperature value in degrees Celsius as an integer – the measured value multiplied by ten. (For example, 56.9 °C is expressed as 569.)

    Not really sure where to go from there...

    Thank you
  • velosprinter
    Junior Member
    • Jul 2008
    • 19

    #2
    The TME units also output an xml page that looks like this:

    <?xml version="1.0" encoding="iso-8859-1" ?>
    - <thermometer>
    <title>Ethernet thermometer TME designed by Papouch s.r.o. - www.papouch.com</title>
    <description>TME1</description>
    <temperature>178</temperature>
    <mintemperature>50</mintemperature>
    <maxtemperature>300</maxtemperature>
    </thermometer>

    Comment

    • MrKen
      Senior Member
      • Oct 2008
      • 652

      #3
      I don't have a Papouch TME Ethernet sensor, but going on the information that you have provided, the following should work.

      I assume that snmpwalk -v 1 -c public <IP> 1.3.6.1.4.1.18248.1.1.1.0
      will give a result like: blah blah:integer: 390 [i.e 39 degrees C]

      Item setup.
      Type: snmpv1 agent
      snmp community: public
      snmp oid: 1.3.6.1.4.1.18248.1.1.1.0
      snmp port: 161
      key: int_temperature
      type of information: Numeric (float)
      units: Deg C [Not 100% sure if Deg C is valid]
      Use custom multiplier: .1 [Changes 390 to 39.0]

      Trigger.

      {hostname:int_temperature.last(0)}>35

      change 35 to whatever degrees you want to set the trigger.

      That should work. Don't forget to configure an Action for the trigger.

      MrKen
      Disclaimer: All of the above is pure speculation.

      Comment

      • velosprinter
        Junior Member
        • Jul 2008
        • 19

        #4
        That was perfect!!!!!

        Working like a charm.

        Thank you very much.

        Comment

        • Volumeman
          Junior Member
          • Dec 2007
          • 2

          #5
          Hello,
          I would like to match two items in a trigger. Trigger trigger-name is "Temperature SP8 Critical High" and the expression I have this:
          {SensorProbe: SP_Temp.last (0)}> {sensorProbe: SP_Temp_Critikal_High.last (0)}

          Both items also exist and provide the correct values​​, only if the currently measured value (SP_Temp.last) is bigger (>) the critical value (SP_Temp_Critikal_High.last) it should come an action. But it does not work. I wear {sensorProbe: SP_Temp.last (0)}> 28, an it works fine. Can anyone help?

          Comment

          Working...