    SNMP Monitoring - ifHCOutOctets or ifOutOctets

    Hi,

    I've started working with Zabbix for SNMP monitoring and I need monitoring two routers: CISCO1941 and CISCO2911.

    Which MIB should I use for the network interface (sent): ifHCOutOctets or ifOutOctets? I'm really confused about this.

    I've attached "Template Module Interfaces SNMPv2" for the routers. I think the value returned for the Zabbix is too low.

    When I run the command below, it returns the value: 62732312475

    snmpwalk -v2c -c Password 10.10.200.11 IF-MIB::ifHCOutOctets.1
    IF-MIB::ifHCOutOctets.1 = Counter64: 62732312475

    What is the unity of this value? How to convert to kbps?


    I would really appreciate any help.
  • Hamardaban
    Senior Member
    Zabbix Certified SpecialistZabbix Certified Professional
    • May 2019
    • 2713

    #2
    Hi !
    ifOutOctets - 32-bit SNMP counters \ ifHCOutOctets - 64-bit SNMP counters.
    For kbps use preprocessing: 1 step = "Change per second" , 2 step Custom multiplier =8 (as in Template)
    More information:
    This document describes answers to commonly asked questions about SNMP counters as they relate to Cisco equipment.

    Comment

    • alexandreroble
      Junior Member
      • Jun 2018
      • 9

      #3
      Hamardaban,

      Thanks for your help!

      I will use the template with the ifHCOutOctets parameter (default).