    Problem with reading SNMP OID HP Power Meter

    I want to get the HP Power Meter in Zabbix with SNMP.

    With snmpwalk I can get the correct power usage from the HP G7 server (166Watt). The HP SNMP agent is also installed.

    snmpwalk -v2c -c public192.168.123.101 1.3.6.1.4.1.232.6.2.15.3
    SNMPv2-SMI::enterprises.232.6.2.15.3.1 = INTEGER:
    166

    Reading the OID in Zabbix gives an error so I tried snmpget:

    snmpget -v2c -c public 192.168.123.101 1.3.6.1.4.1.232.6.2.15.3
    SNMPv2-SMI::enterprises.232.6.2.15.3.1 = No Such Instance currently exists at this OID


    Adding the digit .1 or .0 after .1.3.6.1.4.1.232.6.2.15.3 also doesn't work.
  • mgielissen
    Junior Member
    • Nov 2009
    • 8

    #2
    Tested with Paessler, also the same error:

    ----------------------- New Test -----------------------
    Paessler SNMP Tester 5.2.3 Computername: DESKTOP-TDC1JNC Interface: (192.168.123.158)
    30-8-2019 17:33:20 (10 ms) : Device: 192.168.123.101
    30-8-2019 17:33:20 (15 ms) : SNMP V2c
    30-8-2019 17:33:20 (20 ms) : Walk 1.3.6.1.4.1.232.6.2.15.3
    30-8-2019 17:33:20 (27 ms) : 1.3.6.1.4.1.232.6.2.15.3.1 = "148" [ASN_INTEGER]

    ----------------------- New Test -----------------------
    Paessler SNMP Tester 5.2.3 Computername: DESKTOP-TDC1JNC Interface: (192.168.123.158)
    30-8-2019 17:33:23 (10 ms) : Device: 192.168.123.101
    30-8-2019 17:33:23 (15 ms) : SNMP V2c
    30-8-2019 17:33:23 (20 ms) : Custom OID .1.3.6.1.4.1.232.6.2.15.3.1
    30-8-2019 17:33:23 (27 ms) : SNMP Datatype: SNMP_EXCEPTION_NOSUCHINSTANCE
    30-8-2019 17:33:23 (35 ms) : -------
    30-8-2019 17:33:23 (41 ms) : Value: No such instance (SNMP error # 223)
    30-8-2019 17:33:23 (48 ms) : Done


    ----------------------- New Test -----------------------
    Paessler SNMP Tester 5.2.3 Computername: DESKTOP-TDC1JNC Interface: (192.168.123.158)
    30-8-2019 17:33:41 (10 ms) : Device: 192.168.123.101
    30-8-2019 17:33:41 (15 ms) : SNMP V2c
    30-8-2019 17:33:41 (20 ms) : Custom OID 1.3.6.1.4.1.232.6.2.15.3.1
    30-8-2019 17:33:41 (27 ms) : SNMP Datatype: SNMP_EXCEPTION_NOSUCHINSTANCE
    30-8-2019 17:33:41 (34 ms) : -------
    30-8-2019 17:33:41 (40 ms) : Value: No such instance (SNMP error # 223)
    30-8-2019 17:33:41 (46 ms) : Done

    Comment

    • Hamardaban
      Senior Member
      Zabbix Certified SpecialistZabbix Certified Professional
      • May 2019
      • 2713

      #3
      try .1.3.6.1.4.1.232.6.2.15.3.1.0