I'm hoping the solution to this problem is simple and I'll just smack my forehead when someone tells me, but it eludes me up to this point.
I have Liebert HVAC units in my server rooms, and have the intellislot cards from them configured to answer SNMP requests. I have great graphs of temperature and humidity, but they use messed up boolean numbers for when the unit is cooling or humidifying. The requests provide an integer value of 2 when "off" and an integer value of 1 when "on." I would like to have a graph that shows when the units run in relation to temperature or humidity, but it's counter-intuitive to have "up" on the graph as off and "down" as running.
If Liebert had used 0 for off and 1 for on like everyone else in the known universe, it would be easy, but alas. Does anyone have any recommendations on how to solve this?
Thanks in advance!
I have Liebert HVAC units in my server rooms, and have the intellislot cards from them configured to answer SNMP requests. I have great graphs of temperature and humidity, but they use messed up boolean numbers for when the unit is cooling or humidifying. The requests provide an integer value of 2 when "off" and an integer value of 1 when "on." I would like to have a graph that shows when the units run in relation to temperature or humidity, but it's counter-intuitive to have "up" on the graph as off and "down" as running.