    APC upsBasicStateOutputState with Trigger

    Hello,

    i use the APC Template NUC2 (9631 Card) from Zabbix Share.
    The template does not recognize if the battery is defect or subtracted.
    The SNMP OID 1.3.6.1.4.1.318.1.1.1.11.1.1.0 is the only info String for this info on Flag 33.
    APC support say the Flag 33 for No Batteries Attached or Defect is the only way to monitor the disaster

    When battery ok and connected is the 64 bit SNMP String:

    0001010000000000001000000000000000000000000000000010000000000000

    When battery defect or not connected is the 64 bit SNMP String:

    0001010000000000001000000000000010000000000000000010000000000000

    My problem is now a trigger set up.
    I have tested the following:

    {Template SNMP APC:upsBasicStateOutputState.regexp(@APC)} >>> With global RegExp APC = (?=^.{32}(1)) = TRUE (The global test Works the Trigger not.

    With lokal regexp in Trigger:

    {Template SNMP APC:upsBasicStateOutputState.regexp((?<=^.{32})(1) )}

    (({Template SNMP APC :upsBasicStateOutputState.regexp((?<=^.{32})})<>0)

    {Template SNMP APC :upsBasicStateOutputState.regexp(^.{32}(1))}


    Nothing works.

    EDIT: Tested on Zabbix: 3.0.5 and 3.2.3 on Debian 8
    Last edited by gerry; 02-01-2017, 11:58.
  • ADvorkin
    Junior Member
    • Jan 2018
    • 27

    #2
    (({Template_APC_NMC2:upsBasicStateOutputState.rege xp(^.{32}1.*)})=1)