Hello, running Zabbix 6.4.14, and using the Cisco Nexus 9000 template and having some issue with values returned for temperature. I have it monitoring Module Temperature Sensor however the value that is returned when I run a test is (as an example), 257, when the actual temperature when looking at the Nexus is 25.7 so it seems there is a missing decimal point in the returned value. So I set up a pre-processing rule of 0.1 which I applied and it works by returning the correct value. The problem is that for other temperature monitors for the Nexus return correct values from the Nexus but the pre-processing rule gets applied to it so gives a very low value causing low temperature alarms (for example outlet/inlet temperature and hotspot temperature). Has anyone else seen this issue? Any ideas of a way around the issue? I can only think of having two nexus templates with one having the pre-processing rule and monitoring the module temperature sensor and the other not having the pre-processing rule.
Any help appreciated
Any help appreciated