    Email message confusing

    I have recently added some RAC Servers and and I have a small confusion regarding the email that I have received when the CPU temp exceeds the threshold value

    Subject:
    Problem: CPU1 Temp: Temperature is above warning threshold: >70

    Message:
    Problem started at 03:58:45 on 2025.07.03
    Problem name: CPU1 Temp: Temperature is above warning threshold: >70
    Host:: HostName_DR IDRAC1
    Severity: Warning
    Operational data: Current value: 63 °C
    Original problem ID: 177125845

    Now as seen above operational data current value is 63 and it says that --- CPU1 Temp: Temperature is above warning threshold: >70 hence it sends a email
    Is this a false positive that the email is fired or am I interpreting the message wrongly
    Appreciate and very grateful if someone can clarify the above

    Thanks and Regards

    simon
  • Markku
    Senior Member
    Zabbix Certified SpecialistZabbix Certified ProfessionalZabbix Certified Expert
    • Sep 2018
    • 1781

    #2
    What are the problem and recovery expressions in the trigger?

    Markku

    Comment

    • sbdcunha
      Junior Member
      • May 2023
      • 20

      #3
      Dear Marku
      thanks for your quick response

      problem expression:

      avg(/Nutanix_DR IDRAC1/sensor.temp.value[temperatureProbeReading.CPU.1.1],5m)>{$TEMP_CRIT:"CPU"}
      or
      last(/Nutanix_DR IDRAC1/sensor.temp.status[temperatureProbeStatus.CPU.1.1])={$TEMP_CRIT_STATUS}
      or
      last(/Nutanix_DR IDRAC1/sensor.temp.status[temperatureProbeStatus.CPU.1.1])={$TEMP_DISASTER_STATUS} zz0.ix1aou670sizz

      recovery expression
      max(/Nutanix_DR IDRAC1/sensor.temp.value[temperatureProbeReading.CPU.1.1],5m)<{$TEMP_CRIT:"CPU"}-3

      The above is what i see..
      appreciate your assistance

      thanks and regards

      simon

      Comment

      • Markku
        Senior Member
        Zabbix Certified SpecialistZabbix Certified ProfessionalZabbix Certified Expert
        • Sep 2018
        • 1781

        #4
        So now you see that it is not just the temperature value item that affects the trigger, also the temperature probe status is considered.

        As mentioned in the configuration manual (https://www.zabbix.com/documentation...iggers/trigger), the problem expression must evaluate to FALSE as well as the recovery expression evaluate to TRUE in order the problem to recover.

        Markku