    Trigger only after multiple failures

    I am trying to avoid triggering alarms unless the failure has happened 3 times sequentially. In this case if the temperature of some coolant is below 35C for three sequential occasions. The base code for a single failure is as follows.

    {Sensors1.ukdc1.dcops:bas700.set2.coolanttemp.last ()}<35

    Suggestions much appreciated
  • gofree
    Senior Member
    Zabbix Certified SpecialistZabbix Certified Professional
    • Dec 2017
    • 400

    #2
    check the docu - count function might work

    Comment

    • cyber
      Senior Member
      Zabbix Certified SpecialistZabbix Certified Professional
      • Dec 2006
      • 4807

      #3
      max value during 3 checks should be less than 35.
      {Sensors1.ukdc1.dcops:bas700.set2.coolanttemp.max( #3)}