Hello,
I have Zabbix 2.2.0 on CentOS 6.5 64 with MySQL. All is running fine and I can pull values from my ILO on a DL 380 G6 server with ILO Firmware 2.23.
If I use the ipmitools command from CentOS I get results back properly as shown below.
# ipmitool -I lanplus -H 10.5.39.211 -L user -U sysadmin sensor list
UID Light | 0x0 | discrete | 0x0080| na | na | na | na | na | na
Sys. Health LED | 0x0 | discrete | 0x0080| na | na | na | na | na | na
Power Supply 1 | 65.000 | Watts | nc | na | na | na | na | na | na
Power Supply 2 | 80.000 | Watts | nc | na | na | na | na | na | na
Power Supplies | 0.000 | unspecified | nc | na | na | na | na | na | na
Fan 1 | 13.720 | unspecified | nc | na | na | na | na | na | na
Fan 2 | 13.720 | unspecified | nc | na | na | na | na | na | na
Fan 3 | 29.400 | unspecified | nc | na | na | na | na | na | na
Fan 4 | 39.592 | unspecified | nc | na | na | na | na | na | na
Fan 5 | 43.512 | unspecified | nc | na | na | na | na | na | na
Fan 6 | 43.512 | unspecified | nc | na | na | na | na | na | na
Fans | 0x0 | discrete | 0x0180| na | na | na | na | na | na
Temp 1 | 27.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 39.000 | 41.000 | 45.000
Temp 2 | 40.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 82.000 | 83.000
Temp 3 | 40.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 82.000 | 83.000
Temp 4 | 35.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 87.000 | 92.000
Temp 5 | 35.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 87.000 | 92.000
Temp 6 | 42.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 87.000 | 92.000
Temp 7 | 40.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 87.000 | 92.000
Temp 8 | 45.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 90.000 | 95.000
Temp 9 | 41.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 65.000 | 70.000
Temp 10 | 47.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 90.000 | 95.000
Temp 11 | 36.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 70.000 | 75.000
Temp 12 | 43.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 90.000 | 95.000
Temp 13 | na | degrees C | na | 0.000 | 0.000 | 0.000 | 0.000 | 70.000 | 75.000
Temp 14 | na | degrees C | na | 0.000 | 0.000 | 0.000 | 0.000 | 70.000 | 75.000
Temp 15 | na | degrees C | na | 0.000 | 0.000 | 0.000 | 0.000 | 70.000 | 75.000
Temp 16 | 32.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 70.000 | 75.000
Temp 17 | 33.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 70.000 | 75.000
Temp 18 | 33.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 70.000 | 75.000
Temp 19 | 30.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 70.000 | 75.000
Temp 20 | 38.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 70.000 | 75.000
Temp 21 | 35.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 80.000 | 85.000
Temp 22 | 35.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 80.000 | 85.000
Temp 23 | 44.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 77.000 | 82.000
Temp 24 | 37.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 70.000 | 75.000
Temp 25 | 38.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 70.000 | 75.000
Temp 26 | 39.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 70.000 | 75.000
Temp 27 | na | degrees C | na | 0.000 | 0.000 | 0.000 | 0.000 | 70.000 | 75.000
Temp 28 | 32.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 70.000 | 75.000
Temp 29 | 35.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 60.000 | 65.000
Temp 30 | 75.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 110.000 | 115.000
Memory | 0x0 | discrete | 0x4080| na | na | na | na | na | na
Power Meter | 168.000 | Watts | cr | na | na | na | na | na | na
However Zabbix is not interpreting the values properly. Take Fan 1 for example. For some reason the HP ILO returns the percentage % of the RPMS of the Fan instead of RPM. You can see the value above for 13.720 % or the details from below:
# ipmitool -I lanplus -H 10.5.39.211 -L user -U sysadmin sensor get "Fan 1"
Locating sensor record...
Sensor ID : Fan 1 (0x6)
Entity ID : 7.1
Sensor Type (Analog) : Fan
Sensor Reading : 13.720 (+/- 0) unspecified
Status : Lower Non-Critical
Lower Non-Recoverable : na
Lower Critical : na
Lower Non-Critical : na
Upper Non-Critical : na
Upper Critical : na
Upper Non-Recoverable : na
The sensor reading also matches what I see from the ILO interface directly.
See attached ILO-1.JPG image.
Now on the Zabbix side I created an entry for it as IPMI Agent
Name: Fan1
Key: Fan1
Host Interface 10.5.39.211:623
IPMI Sensor: Fan1
Type: Numeric (float) (I have also tried different combinations even Text to see if makes any difference)
The values appearing in Zabbix is just "1" which cannot be correct. The same for other values like Power Meter.
# ipmitool -I lanplus -H 10.5.39.211 -L user -U sysadmin sensor get "Power Meter"
Locating sensor record...
Sensor ID : Power Meter (0x2c)
Entity ID : 7.10
Sensor Type (Analog) : Current
Sensor Reading : 166 (+/- 0) Watts
Status : Lower Critical
Lower Non-Recoverable : na
Lower Critical : na
Lower Non-Critical : na
Upper Non-Critical : na
Upper Critical : na
Upper Non-Recoverable : na
I have Power Meter defined in Zabbix also as an IPMI Agent, numeric (unsigned) and the results I get are "Power Meter Mar 30th, 2014 04:58:59 PM 2 Watts"
Values are also incorrect for all the Fans and Power. The Temp values seens to be correct.
Any ideas what can be causing this?
Regards,
Paul Aviles
I have Zabbix 2.2.0 on CentOS 6.5 64 with MySQL. All is running fine and I can pull values from my ILO on a DL 380 G6 server with ILO Firmware 2.23.
If I use the ipmitools command from CentOS I get results back properly as shown below.
# ipmitool -I lanplus -H 10.5.39.211 -L user -U sysadmin sensor list
UID Light | 0x0 | discrete | 0x0080| na | na | na | na | na | na
Sys. Health LED | 0x0 | discrete | 0x0080| na | na | na | na | na | na
Power Supply 1 | 65.000 | Watts | nc | na | na | na | na | na | na
Power Supply 2 | 80.000 | Watts | nc | na | na | na | na | na | na
Power Supplies | 0.000 | unspecified | nc | na | na | na | na | na | na
Fan 1 | 13.720 | unspecified | nc | na | na | na | na | na | na
Fan 2 | 13.720 | unspecified | nc | na | na | na | na | na | na
Fan 3 | 29.400 | unspecified | nc | na | na | na | na | na | na
Fan 4 | 39.592 | unspecified | nc | na | na | na | na | na | na
Fan 5 | 43.512 | unspecified | nc | na | na | na | na | na | na
Fan 6 | 43.512 | unspecified | nc | na | na | na | na | na | na
Fans | 0x0 | discrete | 0x0180| na | na | na | na | na | na
Temp 1 | 27.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 39.000 | 41.000 | 45.000
Temp 2 | 40.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 82.000 | 83.000
Temp 3 | 40.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 82.000 | 83.000
Temp 4 | 35.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 87.000 | 92.000
Temp 5 | 35.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 87.000 | 92.000
Temp 6 | 42.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 87.000 | 92.000
Temp 7 | 40.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 87.000 | 92.000
Temp 8 | 45.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 90.000 | 95.000
Temp 9 | 41.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 65.000 | 70.000
Temp 10 | 47.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 90.000 | 95.000
Temp 11 | 36.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 70.000 | 75.000
Temp 12 | 43.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 90.000 | 95.000
Temp 13 | na | degrees C | na | 0.000 | 0.000 | 0.000 | 0.000 | 70.000 | 75.000
Temp 14 | na | degrees C | na | 0.000 | 0.000 | 0.000 | 0.000 | 70.000 | 75.000
Temp 15 | na | degrees C | na | 0.000 | 0.000 | 0.000 | 0.000 | 70.000 | 75.000
Temp 16 | 32.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 70.000 | 75.000
Temp 17 | 33.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 70.000 | 75.000
Temp 18 | 33.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 70.000 | 75.000
Temp 19 | 30.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 70.000 | 75.000
Temp 20 | 38.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 70.000 | 75.000
Temp 21 | 35.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 80.000 | 85.000
Temp 22 | 35.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 80.000 | 85.000
Temp 23 | 44.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 77.000 | 82.000
Temp 24 | 37.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 70.000 | 75.000
Temp 25 | 38.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 70.000 | 75.000
Temp 26 | 39.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 70.000 | 75.000
Temp 27 | na | degrees C | na | 0.000 | 0.000 | 0.000 | 0.000 | 70.000 | 75.000
Temp 28 | 32.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 70.000 | 75.000
Temp 29 | 35.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 60.000 | 65.000
Temp 30 | 75.000 | degrees C | ok | 0.000 | 0.000 | 0.000 | 0.000 | 110.000 | 115.000
Memory | 0x0 | discrete | 0x4080| na | na | na | na | na | na
Power Meter | 168.000 | Watts | cr | na | na | na | na | na | na
However Zabbix is not interpreting the values properly. Take Fan 1 for example. For some reason the HP ILO returns the percentage % of the RPMS of the Fan instead of RPM. You can see the value above for 13.720 % or the details from below:
# ipmitool -I lanplus -H 10.5.39.211 -L user -U sysadmin sensor get "Fan 1"
Locating sensor record...
Sensor ID : Fan 1 (0x6)
Entity ID : 7.1
Sensor Type (Analog) : Fan
Sensor Reading : 13.720 (+/- 0) unspecified
Status : Lower Non-Critical
Lower Non-Recoverable : na
Lower Critical : na
Lower Non-Critical : na
Upper Non-Critical : na
Upper Critical : na
Upper Non-Recoverable : na
The sensor reading also matches what I see from the ILO interface directly.
See attached ILO-1.JPG image.
Now on the Zabbix side I created an entry for it as IPMI Agent
Name: Fan1
Key: Fan1
Host Interface 10.5.39.211:623
IPMI Sensor: Fan1
Type: Numeric (float) (I have also tried different combinations even Text to see if makes any difference)
The values appearing in Zabbix is just "1" which cannot be correct. The same for other values like Power Meter.
# ipmitool -I lanplus -H 10.5.39.211 -L user -U sysadmin sensor get "Power Meter"
Locating sensor record...
Sensor ID : Power Meter (0x2c)
Entity ID : 7.10
Sensor Type (Analog) : Current
Sensor Reading : 166 (+/- 0) Watts
Status : Lower Critical
Lower Non-Recoverable : na
Lower Critical : na
Lower Non-Critical : na
Upper Non-Critical : na
Upper Critical : na
Upper Non-Recoverable : na
I have Power Meter defined in Zabbix also as an IPMI Agent, numeric (unsigned) and the results I get are "Power Meter Mar 30th, 2014 04:58:59 PM 2 Watts"
Values are also incorrect for all the Fans and Power. The Temp values seens to be correct.
Any ideas what can be causing this?
Regards,
Paul Aviles