    Zabbix v7.2.1, APC UPS battery lifetime not okay

    Hi there,

    I've recently upgraded my entire distributed Zabbix infrastructure (server + proxies) to the latest version, 7.2.1. Added a brand-new site with its own v7.2.1 proxy.

    There is an APC Smart-UPS SRT 3000 on the network. The UPS reports the following when querying battery health:

    Click image for larger version

Name:	1.png
Views:	739
Size:	7.1 KB
ID:	496611

    None of the bits are "1", therefore the battery is reported by the UPS as healthy.
    Testing the item returns the same:

    Click image for larger version

Name:	2.png
Views:	501
Size:	38.1 KB
ID:	496612

    The trigger also seems to work:

    Click image for larger version

Name:	3.png
Views:	495
Size:	19.7 KB
ID:	496613

    Click image for larger version

Name:	4.png
Views:	492
Size:	19.2 KB
ID:	496614
    ​​
    Yet, I it is still telling me that the battery lifetime is not okay:

    Click image for larger version

Name:	5.png
Views:	515
Size:	15.9 KB
ID:	496615

    I tested with the generic "APC UPS by SNMP", as well as the "APC Smart-UPS 3000 XLM by SNMP" templates, both pre-canned official Zabbix templates.

    From my research it looks like it's been a problem for years throughout a number of Zabbix releases, and despite some claiming that it's been fixed in a prior version, it isn't - see https://www.zabbix.com/forum/zabbix-...mplate-apc-ups. I've been battling this problem since day 1. Zabbix 6.4 was the latest at the time. Never been able to solve it, and now, at v7.2.1, it still persists.

    Any pointers would be very much appreciated.

    Thank you.​​
  • peperinopomuro
    Junior Member
    • Jan 2025
    • 2

    #2
    Hi there! I am having the same issue. Did you find a solution?

    Comment

    • markfree
      Senior Member
      • Apr 2019
      • 868

      #3
      I can't really confirm this because I don't have such a UPS to test with, but it seems that the regex in the "find" function is wrong. The trigger becomes true because the find function always finds the 0 in the octet string returned by the UPS.

      Since that is an official template, you may be able suggest improvements to Zabbix.

      Comment

      • cyber
        Senior Member
        Zabbix Certified SpecialistZabbix Certified Professional
        • Dec 2006
        • 4807

        #4

        Totally agree... that regex there "^(0)[0|1]{15}$" .. it will not match only if it starts with 1... and rest of 15 places, it may contain 0,1 or |, which also includes "all zeros"
        I think that prototype should be ...
        Code:
        find(/APC UPS by SNMP/battery.pack.cartridge_health[upsHighPrecBatteryPackCartridgeHealth.{#BATTERY_PACK}.{#CARTRIDGE_INDEX}],,"regexp","^(0)(0{15})$")=0
        Then it will react, when there is at least 1 non-zero value within those 15 places... and it all starts with 0, but then it migth aswell be ".... ,"regexp","^(0{16})$")=0" same as for "Battery status not ok" trigger prototype... Just the item is different.

        Other question is, why there is at all 16 bits in that bitmap...:P Mib only describes 7 ... https://mibs.observium.org/mib/Power...artridgeHealth
        The battery cartridge health.
        bit 0 Battery lifetime okay
        bit 1 Battery lifetime near end, order replacement cartridge
        bit 2 Battery lifetime exceeded, replace battery
        bit 3 Battery lifetime near end acknowledged, order replacement cartridge
        bit 4 Battery lifetime exceeded acknowledged, replace battery
        bit 5 Battery measured lifetime near end, order replacement cartridge
        bit 6 Battery measured lifetime near end acknowledged, order replacement cartridge

        Comment

        • peperinopomuro
          Junior Member
          • Jan 2025
          • 2

          #5
          I'm not sure if I did the right thing. But in the discovery rule for "External Battery Packs Discovery" I change the filter to: Cartridge Status matches "^1000000000000000$" and now I only have the real battery packs that I have in every UPS. Before this the discovery was finding a lot of battery packs that I didn't had.


          Comment

          • jlinthicum@caesars.com
            Junior Member
            • Oct 2024
            • 3

            #6
            We have many SMARTUPS6000 units and are experiencing both issues, some units find batteries that don't exist, and all units find bad batteries 3.1 - 3.2 - 2.2 - 2.1 - 1.1 - always show "Battery Status is Not OK" Can anyone confirm if changing the Regex to what Cyber indicated above fixed the issue for them?

            Comment


            • markfree
              markfree commented
              Editing a comment
              Try it out and tell us if it works.
          • jlinthicum@caesars.com
            Junior Member
            • Oct 2024
            • 3

            #7
            It did not work for us unfortunately. we are disabling that trigger for now in our templates and may open an official support ticket with Zabbix.

            Comment

            • Tyler
              Junior Member
              • Apr 2025
              • 1

              #8
              The solution for this I've got was I modified the template to be filtered to (Regex and Regex).

              One to match that it contains only 0s and a single 1
              ^(0{0,15}10{0,15})$
              A Second to match the desired/expected length of 16
              ^([01]{16})$

              If it fills both conditions, it will be the expected 16 length of 0 or 1 while also containing at least one number 1.



              Click image for larger version

Name:	image.png
Views:	365
Size:	46.6 KB
ID:	501853

              Comment

              • dvt
                Junior Member
                • Jun 2025
                • 1

                #9
                Tyler's solution worked for me. I didn't have issues until I added an APC Smart-UPS SRT 3000 running firmware 16.5 to the system. My older Smart-UPS 3000 running 09.3 dont seem to have the discovery issue and stay at 26 items rather than 31.

                Comment

                • ezoltan
                  Junior Member
                  • Feb 2024
                  • 24

                  #10
                  Okay folks, I think I have identified the root cause. The UPS only has an internal battery pack, and the battery pack has room for two cartridges. One cartridge is present while the second is missing. This is indicated by the following result when queried via SNMP:

                  [{"{#SNMPINDEX}":"1.1.1","{#CARTRIDGE_STATUS}":" 100 0000000000000","{#BATTERY_PACK}":"1","{#CARTRIDGE_ INDEX}":"1"},
                  {"{#SNMPINDEX}":"1.1.2","{#CARTRIDGE_STATUS}":" 000 0000000000000","{#BATTERY_PACK}":"1","{#CARTRIDGE_ INDEX}":"2"},
                  {"{#SNMPINDEX}":"2.1.1","{#CARTRIDGE_STATUS}":" "," {#BATTERY_PACK}":"2","{#CARTRIDGE_INDEX}":"1"},
                  {"{#SNMPINDEX}":"2.1.2","{#CARTRIDGE_STATUS}":" "," {#BATTERY_PACK}":"2","{#CARTRIDGE_INDEX}":"2"},
                  {"{#SNMPINDEX}":"3.1.1","{#CARTRIDGE_STATUS}":" "," {#BATTERY_PACK}":"3","{#CARTRIDGE_INDEX}":"1"},
                  {"{#SNMPINDEX}":"3.1.2","{#CARTRIDGE_STATUS}":" "," {#BATTERY_PACK}":"3","{#CARTRIDGE_INDEX}":"2"},
                  {"{#SNMPINDEX}":"4.1.1","{#CARTRIDGE_STATUS}":" "," {#BATTERY_PACK}":"4","{#CARTRIDGE_INDEX}":"1"},
                  {"{#SNMPINDEX}":"4.1.2","{#CARTRIDGE_STATUS}":" "," {#BATTERY_PACK}":"4","{#CARTRIDGE_INDEX}":"2"},
                  {"{#SNMPINDEX}":"5.1.1","{#CARTRIDGE_STATUS}":" "," {#BATTERY_PACK}":"5","{#CARTRIDGE_INDEX}":"1"},
                  {"{#SNMPINDEX}":"5.1.2","{#CARTRIDGE_STATUS}":" "," {#BATTERY_PACK}":"5","{#CARTRIDGE_INDEX}":"2"},
                  {"{#SNMPINDEX}":"6.1.1","{#CARTRIDGE_STATUS}":" "," {#BATTERY_PACK}":"6","{#CARTRIDGE_INDEX}":"1"},
                  {"{#SNMPINDEX}":"6.1.2","{#CARTRIDGE_STATUS}":" "," {#BATTERY_PACK}":"6","{#CARTRIDGE_INDEX}":"2"},
                  {"{#SNMPINDEX}":"7.1.1","{#CARTRIDGE_STATUS}":" "," {#BATTERY_PACK}":"7","{#CARTRIDGE_INDEX}":"1"},
                  {"{ #SNMPINDEX}":"7.1.2","{#CARTRIDGE_STATUS}":"","{#B ATTERY_PACK}":"7","{#CARTRIDGE_INDEX}":"2"},
                  {"{#SNMPINDEX}":"8.1.1","{#CARTRIDGE_STATUS}":" "," {#BATTERY_PACK}":"8","{#CARTRIDGE_INDEX}":"1"},
                  {"{#SNMPINDEX}":"8.1.2","{#CARTRIDGE_STATUS}":" "," {#BATTERY_PACK}":"8","{#CARTRIDGE_INDEX}":"2"},
                  {"{#SNMPINDEX}":"9.1.1","{#CARTRIDGE_STATUS}":" "," {#BATTERY_PACK}":"9","{#CARTRIDGE_INDEX}":"1"},
                  {"{#SNMPINDEX}":"9.1.2","{#CARTRIDGE_STATUS}":" "," {#BATTERY_PACK}":"9","{#CARTRIDGE_INDEX}":"2"},
                  {"{#SNMPINDEX}":"10.1.1","{#CARTRIDGE_STATUS}": "", "{#BATTERY_PACK}":"10","{#CARTRIDGE_INDEX}":"1 "},
                  {"{#SNMPINDEX}":"10.1.2","{#CARTRIDGE_STATUS}": "", "{#BATTERY_PACK}":"10","{#CARTRIDGE_INDEX}":"2 "},
                  {"{#SNMPINDEX}":"11.1.1","{#CARTRIDGE_STATUS}": "", "{#BATTERY_PACK}":"11","{#CARTRIDGE_INDEX}":"1 "},
                  {"{#SNMPINDEX}":"11.1.2","{#CARTRIDGE_STATUS}": "", "{#BATTERY_PACK}":"11","{#CARTRIDGE_INDEX}":"2 "}]

                  From what I read, the string of 16 zeroes for CARTRIDGE_INDEX 2 means that the slot for that cartridge is not populated. Having a non-null value returned and bit #0 set to 0 fools Zabbix to believe that we do have a cartridge _and_ it is unhealthy.

                  Apparently according to APC parlance a bitmap of 16 zeroes means no cartridge/empty slot.

                  This isn't confirmed by APC, but rather the conclusion based on googling it.

                  Basically we should instruct Zabbix to ignore entries with 16 zeroes in the CARTRIDGE_INDEX field. But that's a double-edge sword: if we happen to have cartridge #2 populated and it indeed is unhealthy then Zabbix would just ignore it. Same issue disabling the trigger.

                  I am at a loss.
                  Last edited by ezoltan; 07-08-2025, 15:12.

                  Comment

                  • markfree
                    Senior Member
                    • Apr 2019
                    • 868

                    #11
                    It seems to me that you can filter out battery packs that are absent.
                    Configure your discovery rule to filter out objects with an absent status.

                    Comment